External RCD/sockets

Former Community Member
Former Community Member

From a house ring main can an external rcd socket be used as a fused spur to a small consumer unit in a garage less than 10m away using 2.5 buried protected cable?  (2 LED strip lights and 4 double sockets in the garage)

Parents
  • Steve Mc: 
     

    Thanks but What caveats? Im coming off a kitchen socket (Not Cooker) to supply the external RCD socket I then want to spur the 2.5 cable to the garage to a small consumer unit.  will the external socket trip if the garage has an earth or mains short?

    no it won't, A fused spur is a switch with a fuse in it not an rcd socket

Reply
  • Steve Mc: 
     

    Thanks but What caveats? Im coming off a kitchen socket (Not Cooker) to supply the external RCD socket I then want to spur the 2.5 cable to the garage to a small consumer unit.  will the external socket trip if the garage has an earth or mains short?

    no it won't, A fused spur is a switch with a fuse in it not an rcd socket