External RCD/sockets

Former Community Member
Former Community Member

From a house ring main can an external rcd socket be used as a fused spur to a small consumer unit in a garage less than 10m away using 2.5 buried protected cable?  (2 LED strip lights and 4 double sockets in the garage)

Parents
  • The circuit should be protected at the consumer unit by a 30 mA RCD, no additional RCDs are required.

Reply
  • The circuit should be protected at the consumer unit by a 30 mA RCD, no additional RCDs are required.