Compliance with 411.3.3 RCDs on Socket Outlets

I have a scenario where we have a standard circuit arrangement. 32A Ring Circuit feeding a number of socket outlets.  An RCBO of 32A/30mA is specified at the DB.  However the outlets also have 10mA RCD's at each outlet.    Whilst there may be issues around nuisance tripping. ITs been suggested that we remove the RCBO and use a standard 32A Type B MCB at the DB.

 IMO this means the circuit would not have RCD protection,  and only the outlets ( or appliance plugged into an outlet would be protected).  So the question I have is would a 32A MCB Ring circuit when serving this arrangement be compliant with the regs?

One concern I have with this is that should an outlet ever be changed for a normal 13A SSO, then the circuit again would be non compliant.   And that in the event of an earth fault (depending on the ZS) it may not achieve the necessary disconnection times for a ring circuit. 

 

Thoughts? 

Parents
  • 10 mA RCDs can be used for compliance with Regulation 411.3.3 of BS 7671, provided the RCD complies with one of the standards listed in Regulation Group 531.4.1.

    What standard do the socket-outlets incorporating RCDs comply with? If it's BS 7288, then  Regulation 531.4.1 does not recognise that standard for RCDs, and therefore removing the device at the origin of the circuit means the circuit would not, technically, comply with BS 7671.

    As a further consideration, is the RCD required for other purposes (e.g. certain requirements for special locations in Part 7, or Regulations 522.6.203 / 522.6.204)? If so, it's likely that the circuit needs to be protected, not the socket-outlet.

Reply
  • 10 mA RCDs can be used for compliance with Regulation 411.3.3 of BS 7671, provided the RCD complies with one of the standards listed in Regulation Group 531.4.1.

    What standard do the socket-outlets incorporating RCDs comply with? If it's BS 7288, then  Regulation 531.4.1 does not recognise that standard for RCDs, and therefore removing the device at the origin of the circuit means the circuit would not, technically, comply with BS 7671.

    As a further consideration, is the RCD required for other purposes (e.g. certain requirements for special locations in Part 7, or Regulations 522.6.203 / 522.6.204)? If so, it's likely that the circuit needs to be protected, not the socket-outlet.