Compliance with 411.3.3 RCDs on Socket Outlets

I have a scenario where we have a standard circuit arrangement. 32A Ring Circuit feeding a number of socket outlets.  An RCBO of 32A/30mA is specified at the DB.  However the outlets also have 10mA RCD's at each outlet.    Whilst there may be issues around nuisance tripping. ITs been suggested that we remove the RCBO and use a standard 32A Type B MCB at the DB.

 IMO this means the circuit would not have RCD protection,  and only the outlets ( or appliance plugged into an outlet would be protected).  So the question I have is would a 32A MCB Ring circuit when serving this arrangement be compliant with the regs?

One concern I have with this is that should an outlet ever be changed for a normal 13A SSO, then the circuit again would be non compliant.   And that in the event of an earth fault (depending on the ZS) it may not achieve the necessary disconnection times for a ring circuit. 

 

Thoughts? 

Parents
  • it said something like additional protection must be provided upstream of the device.

    I understand it does, but the original wording I think was in a paragraph that was discussing the situation where the circuit upstream of the socket itself required additional protection (e.g. T&E concealed in walls) but it seems the clarity was lost during a revision. Why on earth the committee behind BS 7288 hasn't issued a corrigendum to make it clear again baffles me - they surely have manufacturers on the committee and an official interpretation that makes their products akin to a chocolate fireguard can't be in their best interests.

      - Andy.

Reply
  • it said something like additional protection must be provided upstream of the device.

    I understand it does, but the original wording I think was in a paragraph that was discussing the situation where the circuit upstream of the socket itself required additional protection (e.g. T&E concealed in walls) but it seems the clarity was lost during a revision. Why on earth the committee behind BS 7288 hasn't issued a corrigendum to make it clear again baffles me - they surely have manufacturers on the committee and an official interpretation that makes their products akin to a chocolate fireguard can't be in their best interests.

      - Andy.