The application of BS 7288 RCDs

The application of BS 7288 SRCDs has cropped up from time to time, so what is their application since BS 7671:2018?

531.3.6 specifies that RCDs for additional protection shall comply with BS 61008, BS 61009, or BS 62423 (type F and type B devices). BS 7288 SRCDs appear to have been acceptable up to and including BS 7671:2008+3 because there is no corresponding paragraph. This is not entirely surprising because BS 7671:2008+3 was published in 2015 whereas the current version of BS 7288 was published during the following year and in essence, it is BS 7288 which rules out SRCDs for additional protection.

Section 1 of BS 7288, Scope, says: SRCDs are only intended to provide supplementary protection downstream of the SRCD. SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.

That begs the question, supplementary to what? It can only be additional protection (provided by a BS 61008, etc. device). So why fit one?

It seems to me that there are two reasons. First, where it is desired to have protection with a sensitivity of 10 mA, perhaps at a workstation where the risk of direct contact is increased; and second, where a second level of protection is required to guard against failure of an upstream RCD.

If anybody can think of another reason for fitting a BS 7288 SRCD, do please speak up.

Parents
  • So (and I too have not yet got a copy of the latest so I am making a bit of a leap) that sounds like we are back to being able to fit RCD sockets as an upgrade to metal trunking so long as the upstream hot wire fuse would clear the Zs and there are no bits of bare single or T and E between the socket and the fuseboard not inside trunking or conduit with holes less than 35mm diameter.
    If so this seems very sensible, lots of factories and so on will be very relieved.
    Mike

    PS can someone say if the 3m bathroom socket has now become 2,5m - it was in the draft but I'd like to know if it survived editing.

Reply
  • So (and I too have not yet got a copy of the latest so I am making a bit of a leap) that sounds like we are back to being able to fit RCD sockets as an upgrade to metal trunking so long as the upstream hot wire fuse would clear the Zs and there are no bits of bare single or T and E between the socket and the fuseboard not inside trunking or conduit with holes less than 35mm diameter.
    If so this seems very sensible, lots of factories and so on will be very relieved.
    Mike

    PS can someone say if the 3m bathroom socket has now become 2,5m - it was in the draft but I'd like to know if it survived editing.