MK LOGIC RAPID FIX

Anyone tried the new MK sockets with lever terminals?

https://www.screwfix.com/p/mk-logic-rapid-fix-13a-2-gang-dp-switched-socket-white-with-white-inserts-1-pack/814ph

Obvious failing to my eyes is only 3 PE terminals - if you're spurring off from a ring and prefer to have a fly-lead to the back box then you're going to need 4. (OK you could loop one of the c.p.c.s through the back box terminal if you're using reduced size c.p.c.s. (e.g. T&E) - but it's a bit messy and probably isn't going to work with full sized c.p.c.s. as most many back box terminals won't take more than one larger conductor).

   - Andy.

Parents
  • EDIT - after a quick look at the video above, there is no “sol”, “r” or “f” marking evident, so it would appear they are suitable for all conductor stranding types?

    If you look at around 4:30 onwards in the video they show Class 1, class 2 and class 5 conductors being connected… 

       - Andy.

Reply
  • EDIT - after a quick look at the video above, there is no “sol”, “r” or “f” marking evident, so it would appear they are suitable for all conductor stranding types?

    If you look at around 4:30 onwards in the video they show Class 1, class 2 and class 5 conductors being connected… 

       - Andy.