MK LOGIC RAPID FIX

Anyone tried the new MK sockets with lever terminals?

https://www.screwfix.com/p/mk-logic-rapid-fix-13a-2-gang-dp-switched-socket-white-with-white-inserts-1-pack/814ph

Obvious failing to my eyes is only 3 PE terminals - if you're spurring off from a ring and prefer to have a fly-lead to the back box then you're going to need 4. (OK you could loop one of the c.p.c.s through the back box terminal if you're using reduced size c.p.c.s. (e.g. T&E) - but it's a bit messy and probably isn't going to work with full sized c.p.c.s. as most many back box terminals won't take more than one larger conductor).

   - Andy.

Parents
  • Former Community Member
    0 Former Community Member

    (OK you could loop one of the c.p.c.s through the back box terminal if you're using reduced size c.p.c.s. (e.g. T&E) - but it's a bit messy and probably isn't going to work with full sized c.p.c.s. as most many back box terminals won't take more than one larger conductor).

    Is the earth terminal in the metal back box a BS 1363 accessory or junction box to BS EN 60670-22?

    If not, should the use of it as part of a ring final circuit be recorded under 133.5 even when looped?

    Regards

    BOD

Reply
  • Former Community Member
    0 Former Community Member

    (OK you could loop one of the c.p.c.s through the back box terminal if you're using reduced size c.p.c.s. (e.g. T&E) - but it's a bit messy and probably isn't going to work with full sized c.p.c.s. as most many back box terminals won't take more than one larger conductor).

    Is the earth terminal in the metal back box a BS 1363 accessory or junction box to BS EN 60670-22?

    If not, should the use of it as part of a ring final circuit be recorded under 133.5 even when looped?

    Regards

    BOD