recording conductor sizes on schedules

Hello all 

what do ‘you’ record on EIC and/or EICR if a circuit has smaller conductor sizes downstream of its run (where origin fuse is adequately protecting)  ?

 

Regards

Habs

 

Parents
  • Two questions (assuming the OCPD can't provide overload protection for the smaller csa conductors):

    1. Can overload current protection be omitted for the smaller csa conductors?

    2. Does the overcurrent protective device provide fault current protection for the smaller csa?

    If the answer to BOTH of those questions is “YES” then there is, most likely, no issue.
    If the answer to EITHER of those is “NO”, it's probably a C3 or a C2 depending on the circumstances.

Reply
  • Two questions (assuming the OCPD can't provide overload protection for the smaller csa conductors):

    1. Can overload current protection be omitted for the smaller csa conductors?

    2. Does the overcurrent protective device provide fault current protection for the smaller csa?

    If the answer to BOTH of those questions is “YES” then there is, most likely, no issue.
    If the answer to EITHER of those is “NO”, it's probably a C3 or a C2 depending on the circumstances.