what do ‘you’ record on EIC and/or EICR if a circuit has smaller conductor sizes downstream of its run (where origin fuse is adequately protecting) ?
Regards
Habs
Hello all
what do ‘you’ record on EIC and/or EICR if a circuit has smaller conductor sizes downstream of its run (where origin fuse is adequately protecting) ?
Regards
Habs
Take, for example, a kitchen radial in 4 sqmm but with switched spurs to under-the-counter single sockets for specified appliances. It would be a waste of copper to make them in 4 sqmm - could even be 1.5 sqmm. I would specify 4 sqmm for the circuit but add a comment in the “remarks” box; e.g. “spurs to named sockets in 2.5 sqmm T&E”.
Take, for example, a kitchen radial in 4 sqmm but with switched spurs to under-the-counter single sockets for specified appliances. It would be a waste of copper to make them in 4 sqmm - could even be 1.5 sqmm. I would specify 4 sqmm for the circuit but add a comment in the “remarks” box; e.g. “spurs to named sockets in 2.5 sqmm T&E”.