BS 1363 13A Socket Continuous Max Load

Let me start by saying this is NOT about the maximum load of a double socket outlet, that has been done before!

At a recent Elex “seminar” Darren Staniforth from Scolmore made a comment that BS1363 socket outlets were only tested for 8A continuous load. This was news to me because my 1995 version of BS1363-2 says for the Temperature rise test the connected load will be 14A for a minimum continuous period of 4hours or longer until stability is reached and max duration of 8hours. 

If I recall the comments at Elex correctly, he then went on to say the latest version of BS1363 made provision for socket outlets to have a continuous load of 13A to cater for equipment like EV chargers ("granny cable") and these “plug and play” 13A hot tubs that seem so popular now. Also that some manufacturers (maybe Scolmore?) were now making socket outlets to accommodate these large loads of long continuous periods.

So my question is, does anybody know what BS 1363-2:2016+A1:2018 says about continuous loads that is different from before? And if there is a change which manufacturers are making socket outlets to the latest standard?

Parents
  • And it would perhaps make sense if in the tests for the EV marked sockets they were to be mated with EV marked plugs and run at a higher current, but they are not. The test currents are the same for normal and EV marked units - the subtle difference in testing is that the EV rated sockets also have to survive a certain number of unplug and plug in events with a load with an inductive power factor, and there is a sustained load test.

    As far as I am aware, there are no design changes to an ‘EV’ marked socket, relative to the standard offerings, rather there are some extra tests, and some letters to be applied.

    I cannot help feeling that it would be better if the ‘EV’ marking was duplicated  on the front, and if the extra tests did involve a higher RMS current..

    Mike.

Reply
  • And it would perhaps make sense if in the tests for the EV marked sockets they were to be mated with EV marked plugs and run at a higher current, but they are not. The test currents are the same for normal and EV marked units - the subtle difference in testing is that the EV rated sockets also have to survive a certain number of unplug and plug in events with a load with an inductive power factor, and there is a sustained load test.

    As far as I am aware, there are no design changes to an ‘EV’ marked socket, relative to the standard offerings, rather there are some extra tests, and some letters to be applied.

    I cannot help feeling that it would be better if the ‘EV’ marking was duplicated  on the front, and if the extra tests did involve a higher RMS current..

    Mike.