Oil Pipe Bonding.

A garden oil tank is made of plastic. It is supported on blocks off the ground. Its plastic covered metal oil pipe runs above ground along a wall into a bungalow to the oil boiler. From a visual inspection I believe that the metal pipe is NOT an extraneous-conductive-part, but have not electrically tested it yet.

But…………..there is an earth electrode at the tank position with a length of badly connected green and yellow wire that earths the metal pipe. Why do tank installers do that? So now do I:

a, Remove the earth electrode

or

b, Main bond the metal oil pipe?

Z.

Parents
  • gkenyon: 
     

    If we are seriously worrying about PME, surely we'd certainly want to avoid diverted Neutral currents … meaning because there's an earth electrode at the tank, it would be preferable for the entire installation to be TT …

    It's what's done at filling stations - and don't forget, this pipe's not buried!

     

    I did not mention that for most of its run the pipe is clipped to a wall at low level, but for the last 3  or 4 metres runs under a concrete path then upwards to the oil tank. I like the idea of TTing the whole installation though. So obvious and simple a solution I had overlooked it.

     

    Z.

Reply
  • gkenyon: 
     

    If we are seriously worrying about PME, surely we'd certainly want to avoid diverted Neutral currents … meaning because there's an earth electrode at the tank, it would be preferable for the entire installation to be TT …

    It's what's done at filling stations - and don't forget, this pipe's not buried!

     

    I did not mention that for most of its run the pipe is clipped to a wall at low level, but for the last 3  or 4 metres runs under a concrete path then upwards to the oil tank. I like the idea of TTing the whole installation though. So obvious and simple a solution I had overlooked it.

     

    Z.