I have been round to a relatives flat and seen he has an old Wylex board with MCBs. His bathroom has no supplementary bonding from what I can see and no RCD protection for his electric shower. how potentially dangerous is this? I know the circuits are fairly short and can see main bonding in place Can only really think if the R2 values are low enough touch voltages should end up being kept low? 

 

 

 

  • I prefer to see an RCD too, it trips before faults get out of hand, but having also lived with many showers without, both nice ones here and wilder looking ones abroad, including some that look similar to that photo I posted with twist joins and so on, I'm trying to reassure the OP that even when it goes wrong and is not earthed it is not that dangerous to the end user so long as the water is of drinking grade. We tend to assume that a non-compliance with the latest regs == lethal danger, and it is not necessarily so.

    And I agree the older RCDS and Vo ELCBs were very well engineered, but in modern money at  £100s  we'd not pay. (and most folk  did not want to pay for them back then either…)

    Mike.

  • Zoomup: 
     

    mapj1: 
     

    well. you need to get the human between two conductive parts at different voltages. 

    Now  I  have seen this happen with a shower actually, where a leak inside caused water to pass over the live terminals and trickle down the wall. At the same time more or less earthed water came out of the exit hose. However, both were high impedance paths and all that was reported was a bit of a tingle when leaning on the tiles and under the shower.

    Amusingly having explained all this to the wide eyed friend who had been the victim,  she said ‘gosh we could have 3 dead bodies in the shower!’ I pointed out that this was unlikely as I for one would not go climbing into a shower cubicle with a corpse already in it without investigating first…

    There is very little risk, unless the shower has exposed metal plumbing, and modern ones do not, the modern way is that the hose is actually rubber lined and screws to a plastic fitting, and the incoming water spigot is also plastic.  If the shower develops an internal leak, stop using it.

    Mike 

    Some showers have a water pressure release valve situated in the exit pipe just before the flexible shower hose to open if the shower head gets blocked. It is sited on a nylon water tube. Recently whilst fault finding I had the experience of getting wet feet. The blinkin thing had opened and water at high pressure issued forth spraying me. To my mind the water could have entered upwards into the electrics as the water outlet is positioned against the wall tiles. I would definitely prefer R.C.D. protection there. I believe that the makers Aqualiga(?) and Gainsborough use these pressure release devices as do others.

     

    Z.

    In the 70s I bought a house with an electric shower, 6kW wow! It was running off a 30 Amp hot fuse wire which I changed to a M.C.B. We got no shocks. After a while I when I could afford it, installed a current operated earth leakage circuit beaker rated at 500mA I seem to remember. It was  a Crabtree big brown/black coloured box. 500mA! Anyway it would have tripped much sooner than a hot wire fuse or M.C.B. if water got into the electrics or the heating element shorted or partially shorted to earth.

     

    Edit. Add. Yes I have just confirmed that the Crabtree E.L.C.B. was a model L60 with a rated sensitivity of 500mA. And it had a test button as well. It was built like a tank and would still operate today as it was of such high quality.

    Z.

  • mapj1: 
     

    well. you need to get the human between two conductive parts at different voltages. 

    Now  I  have seen this happen with a shower actually, where a leak inside caused water to pass over the live terminals and trickle down the wall. At the same time more or less earthed water came out of the exit hose. However, both were high impedance paths and all that was reported was a bit of a tingle when leaning on the tiles and under the shower.

    Amusingly having explained all this to the wide eyed friend who had been the victim,  she said ‘gosh we could have 3 dead bodies in the shower!’ I pointed out that this was unlikely as I for one would not go climbing into a shower cubicle with a corpse already in it without investigating first…

    There is very little risk, unless the shower has exposed metal plumbing, and modern ones do not, the modern way is that the hose is actually rubber lined and screws to a plastic fitting, and the incoming water spigot is also plastic.  If the shower develops an internal leak, stop using it.

    Mike 

    Some showers have a water pressure release valve situated in the exit pipe just before the flexible shower hose to open if the shower head gets blocked. It is sited on a nylon water tube. Recently whilst fault finding I had the experience of getting wet feet. The blinkin thing had opened and water at high pressure issued forth spraying me. To my mind the water could have entered upwards into the electrics as the water outlet is positioned against the wall tiles. I would definitely prefer R.C.D. protection there.

     

    Here is the pressure release valve. The short spur is positioned against the tiled wall and when open spurts water in all directions.

     

    Z.

  • well. you need to get the human between two conductive parts at different voltages. 

    Now  I  have seen this happen with a shower actually, where a leak inside caused water to pass over the live terminals and trickle down the wall. At the same time more or less earthed water came out of the exit hose. However, both were high impedance paths and all that was reported was a bit of a tingle when leaning on the tiles and under the shower.

    Amusingly having explained all this to the wide eyed friend who had been the victim,  she said ‘gosh we could have 3 dead bodies in the shower!’ I pointed out that this was unlikely as I for one would not go climbing into a shower cubicle with a corpse already in it without investigating first…

    There is very little risk, unless the shower has exposed metal plumbing, and modern ones do not, the modern way is that the hose is actually rubber lined and screws to a plastic fitting, and the incoming water spigot is also plastic.  If the shower develops an internal leak, stop using it.

    Mike 

  • That’s mad!! So in theory what are the hazards of an electrical shower wich is not accessible but no RCD protecte and no supplementry bonding? my guess is it only becomes dangerous if there’s a fault which we are exposed to and we touch another bit of earthed metal work ie a tap which is not as well earthed to keep the touch voltage down? 

  • Is the shower made of metal ? many modern ones seem to be entirely plastic, and while they do connect the element body to ground, to trip an RCD if the element body corrodes, it is not an accessible part and given the water path length between the element and the user, it could probably be a lot more live, and not pose a hazard.

    In less fussy parts of the world, it is common to heat water with an element in a way that the live hot metal is directly immersed. So long as the water stays drinkably pure, there is negligible shock risk, despite visitors calling them suicide showers..

    Big clive took one to bits a while back…

    The wiring is often a bit rough by UK standards, this is typical. It is not dangerous to the natives, nor to the careful visitor.

    0d55aae9c6e8c2429c35fd00caf6b89b-original-shower_southamerica.png

    I suggest the original poster  need not worry to much, unless it looks worse than this. 

     

    Mike

     

     

  • Can you please explain, for instance, the current path of a fault and how the 50V between an exposed-c-p and an extraneous-c-p is calculated or achieved.

    Calculation (current path and assumptions)

    Step 1 decide the maximum current that may flow to earth (live to CPC )without operating ADS quickly.

    (if say  breaker is 40A perhaps a 50A current) 

    Step 2 measure the resistance between the CPC and the non-bonded part.

    (let us assume the non bonded part is connected to the MET by some moderate resistance)

    Step 3 Assume (an this is the biggy)  that in the worst case fault, all the current in step 1 flows in the resistance of step 2, and multiply both numbers to get a maximum voltage.

    perhaps the cpc is 1 ohm from fault point to the MET and the point of fault rises 50V relative to MET during fault.

    less than 50 ?

    more than 50  ?

     In reality this over estimates the problem, as the unbonded part may not be connected to the MET at the other end of the CPC, so the resistance may not be the full R2..

    Mike

  • If the extraneous conductive parts are caught by the MPB then during a fault of negligible impedance, the fault current is considered to be confined to the cpc and the fault current magnitude being the current required to disconnect the CPD in 5s or +0.1s in the case of mcbs. The actual current may be more but the trade off is that disconnection will be quicker. The touch voltage experienced can therefore be assessed to be the voltage drop along the cpc referenced to the MET.

    Similarly when supplementary bonding is in place, then all of the fault current required to disconnect the CPD is considered to be confined to the supplementary bond. The Ut being apparent across it.

  •  

    Yes, but how?

    Can you please explain, for instance, the current path of a fault and how the 50V between an exposed-c-p and an extraneous-c-p is calculated or achieved.

  • geoffsd: 
     

    Could someone please explain how the R<50/Ia actually affects anything and makes a difference?

    It's intended to keep the voltage between simultaneously-accessible exposed-conductive-parts at less than 50 V for faults that last up to 5 seconds (with Type B and Type C mcb's and RCBO's however, it's 50 V for faults above 0.1 seconds), so that if you are unfortunate enough to be touching the two parts when a fault occurs it is, to all intents and purposes less of a shock (pun certainly intended).

    It won't make a difference to someone in Zone 0 of a bath, but in general it provides a reasonable level of protection, effectively limiting the touch voltage for long-duration faults to ELV level (higher current, quicker operating time, but still well below the 230 V level so reasonable).

    In medical locations of Group 1 or Group 2, the resistance is modified to  0.2 ohms - but see also Regulation 710.411.3.2.5 where the voltage available between simultaneously accessible exposed- and/or extraneous-conductive-parts from a fault in a Group 1 or Group 2 medical location must be limited for ALL faults to 25 V AC or 60 V DC.