B and B+ Type R.C.D.s.

There are so many different types of R.C.D.s available these days. Some are very expensive. I used to like a fully loaded R.C.B.O. consumer unit with A.C. type 30mA R.C.B.O.s. Now it may not be possible to fully comply without spending a lot of cash. And are the newer types of R.C.D. types available as an affordable R.C.B.O. equivilent? Might we revert back to split load consumer units with type A.C. R.C.B.O.s for some circuits and a bank of M.C.B.s on the second half protected by just one type A, F, B or B+ R.C.D? 

 

Quick selection of RCD type
Typical applications Typical loads RCD selection
General applications
(household, commercial, industrial)

Oven, lights Type AC
Dimmer, primary switch mode power supply, multi-speed motors, fan, oven, air conditioning
supplied at 50/60Hz with part of the sinus wave Type A
Extended lighting circuits, computers supply and other lines subject to unwanted tripping Type A-APR
Household appliances and motors with single phase inverters Type F
Industrial applications Motors driven by three-phase inverters Type B
Motors driven by three-phase inverters with very high frequency Type B+

 

Z.

Parents
  • But why does your plug-in oven need additional protection, ain't the earthing good enough?

    The oven might not, but the socket/circuit does -  BS 7671 demands it, as I'm sure you're aware. Earthing doesn't protect against direct contact (nails into concealed cables) or high Zs (long extension leads fed from the socket).

       - Andy.

Reply
  • But why does your plug-in oven need additional protection, ain't the earthing good enough?

    The oven might not, but the socket/circuit does -  BS 7671 demands it, as I'm sure you're aware. Earthing doesn't protect against direct contact (nails into concealed cables) or high Zs (long extension leads fed from the socket).

       - Andy.