PV greater than 4 kw.

How viable would be domestic PV systems of more than 4 kw ?

I appreciate that such systems require more complex approvals, but are not prohibited.

The proposed installation is a new large single floor home. A 100 amp 3 phase supply is to be requested. Options being considered are about 10 kw PER PHASE, plenty of roof area.

Parents
  • For a single supply off an HV transformer, it is probably going to work. At the end of a long LV feeder, the voltage rise caused by the generation may not be acceptable. 

    Regards,

    Alan. 

Reply
  • For a single supply off an HV transformer, it is probably going to work. At the end of a long LV feeder, the voltage rise caused by the generation may not be acceptable. 