Been fault finding on my old combi and having solved the problem I would like to share the solution with those who are still running the old Baxi Water Hotter!

Model of boiler is BAXI 105E combi - Not a condensing combi. This model is around 20 years old.

Nature of fault - No hot water, fan failure fault light on, and flame failure fault light on.

I initially changed the complete diverter valve assembly because the original one was leaking and badly corroded, although this was not actually causing the fault.

I traced the fault to a relay on the pcb which actuates the fan. For information, the relay is marked RL.1

This applies to a Honeywell pcb with the following markings printed on it -

CE 00518L 1810

CS0118E-LS

TYPE:MIDINT00

CD 995099 2

CD 565599 2 

I sourced a replacement relay from ebay, in fact I bought 2, since there are 2 identical relays on the pcb so I got a spare.

Relay part no details - 

TAKAMISAWA JV24S-KT

5A 30VDC

250VAC

SPST

Coil voltage is 30VDC, cantact voltage rating is 250VAC

I unsoldered the original relay and connected 30VDC across the coil and a multi-meter set to ohms across the contacts - result was open circuit.

I repeated the process with the new relay and got continuity across the contacts and a satisfactory click as the coil energised.

I had a spare pcb but that didn't work at all when I just did a straight swap. Anyway I hope someone finds this info useful.

Parents
  • whjohnson: 
     

    I didn't know that you could not work on boiler electrics for hire or reward even if you didn't remove any gas-tight covers. Surely you don't have to be Gas Safe registered in order to take off the front cover to connect in the mains supply and any control wiring do you?

    I was going to look at getting a new boiler, and thought I'd fit it to the wall and just let the Gas Safe bloke come and connect up the gas side. So are you saying that a new boiler or any spare parts cannot be purchased online without the provision of proof of Gas Safe membership?

    I used to fit my own boilers' and get a corgi, (yes back then…), to connect the gas, never had a problem BUT, nowadays' you are not allowed to removed the sealed cover, or tamper with the gas supply.

    As for fitting the flue… I have been told, many times, by ‘plumbers’ that all you need to be is, as stated above… ‘competent!'

Reply
  • whjohnson: 
     

    I didn't know that you could not work on boiler electrics for hire or reward even if you didn't remove any gas-tight covers. Surely you don't have to be Gas Safe registered in order to take off the front cover to connect in the mains supply and any control wiring do you?

    I was going to look at getting a new boiler, and thought I'd fit it to the wall and just let the Gas Safe bloke come and connect up the gas side. So are you saying that a new boiler or any spare parts cannot be purchased online without the provision of proof of Gas Safe membership?

    I used to fit my own boilers' and get a corgi, (yes back then…), to connect the gas, never had a problem BUT, nowadays' you are not allowed to removed the sealed cover, or tamper with the gas supply.

    As for fitting the flue… I have been told, many times, by ‘plumbers’ that all you need to be is, as stated above… ‘competent!'