There is an article in PE and I have just received it via email.
I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems
John Peckham:
Evening All
You may find this article in IET Wiring Matters more useful.
https://electrical.theiet.org/wiring-matters/years/2021/86-july-2021/hot-tubs/
It does cover PME earthing.
If you register with the IET to receive Wiring Matters it will come to you via an email.
JP
If we're worried about perceived electric shocks - where it sounds like having an earthing system even a few volts above true Earth could be a problem - then is a TT system really any better than PME? On a TT system earth leakage currents (either from filters etc or just damp getting into things) will raise the voltage on the Earthing system (Ohm's Law - leakage current x Ra) - say 50mA and 200 Ohms would produce 10V - and for indefinite lengths of time. BS 7671 only require we keep it below 50V.
- Andy.
John Peckham:
Evening All
You may find this article in IET Wiring Matters more useful.
https://electrical.theiet.org/wiring-matters/years/2021/86-july-2021/hot-tubs/
It does cover PME earthing.
If you register with the IET to receive Wiring Matters it will come to you via an email.
JP
If we're worried about perceived electric shocks - where it sounds like having an earthing system even a few volts above true Earth could be a problem - then is a TT system really any better than PME? On a TT system earth leakage currents (either from filters etc or just damp getting into things) will raise the voltage on the Earthing system (Ohm's Law - leakage current x Ra) - say 50mA and 200 Ohms would produce 10V - and for indefinite lengths of time. BS 7671 only require we keep it below 50V.
- Andy.