PE advice by Napit (hot tubs)

There is an article in PE and I have just received it via email.

I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems

Parents
  • Does BS 7671 really require we keep the touch voltage below 50 V?

    For TT systems that use RCDs, and for ‘persistent’ touch voltages , yes - 411.5.3 (ii).

    The TT systems that have such low loop impedances that overcurrent devices can be used, there isn't a specified limit, but as the system then approximates to TN systems any reasonable leakage current isn't likely to do any harm.

        - Andy.

Reply
  • Does BS 7671 really require we keep the touch voltage below 50 V?

    For TT systems that use RCDs, and for ‘persistent’ touch voltages , yes - 411.5.3 (ii).

    The TT systems that have such low loop impedances that overcurrent devices can be used, there isn't a specified limit, but as the system then approximates to TN systems any reasonable leakage current isn't likely to do any harm.

        - Andy.