There is an article in PE and I have just received it via email.

I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems

Parents
  • where the fault current exceeds the residual operating current, the touch voltage may also exceed 50 V until the device trips.

    But the touch voltage won't persist - as the RCD will trip. Remember I was comparing the situation with the problem of perceived shocks on PME systems - due to voltage drop along PEN conductor in normal, non-fault, conditions.

    We say to avoid PME partly because perceived electric shocks from the PEN conductor which can potentially be up to (say) 18.4V above Earth, yet we recommend a TT system - possibly TT'd an entire installation - where there's no guarantee that voltages of anything up to to 50V might persist. 

      - Andy.

     

Reply
  • where the fault current exceeds the residual operating current, the touch voltage may also exceed 50 V until the device trips.

    But the touch voltage won't persist - as the RCD will trip. Remember I was comparing the situation with the problem of perceived shocks on PME systems - due to voltage drop along PEN conductor in normal, non-fault, conditions.

    We say to avoid PME partly because perceived electric shocks from the PEN conductor which can potentially be up to (say) 18.4V above Earth, yet we recommend a TT system - possibly TT'd an entire installation - where there's no guarantee that voltages of anything up to to 50V might persist. 

      - Andy.

     