PE advice by Napit (hot tubs)

There is an article in PE and I have just received it via email.

I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems

Parents
  • But also, this is only the earth electrode resistance, not the effective resistance from the transformer earth to the point at which you are standing … 

    Which is probably just what you want if you want to calculate the voltage between the MET and the ground at the consumer's installation - it's less likely that the victim will have long enough arms to be touching part of the consumer's installation while stood next to the substation.

        - Andy.

Reply
  • But also, this is only the earth electrode resistance, not the effective resistance from the transformer earth to the point at which you are standing … 

    Which is probably just what you want if you want to calculate the voltage between the MET and the ground at the consumer's installation - it's less likely that the victim will have long enough arms to be touching part of the consumer's installation while stood next to the substation.

        - Andy.