I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems
mapj1:
Very low electrode resistances are not always good, nor is it always safe to omit the RCD and rely on a fuse or MCB if you have them.
Mike
And vice-versa … in a TT system if you take the simple path for the Zs loop through the main consumer earth electrode resistance Ra (or in a TN system, the supplier's earthing terminal only) as the “worst case” for automatic disconnection, it's not always safe to assume it's the “worst case” for prospective earth fault current once supplementary electrodes are connected. Yet in TT systems this is often ignored “because the RCD does the job” in an earth fault …
mapj1:
Very low electrode resistances are not always good, nor is it always safe to omit the RCD and rely on a fuse or MCB if you have them.
Mike
And vice-versa … in a TT system if you take the simple path for the Zs loop through the main consumer earth electrode resistance Ra (or in a TN system, the supplier's earthing terminal only) as the “worst case” for automatic disconnection, it's not always safe to assume it's the “worst case” for prospective earth fault current once supplementary electrodes are connected. Yet in TT systems this is often ignored “because the RCD does the job” in an earth fault …