The dreaded bonding again

Sorry for this but my boiler recently had her annual service all was well except they said I don't have any bonding in place except I think I do the gas main is bonded in the meter cupboard and the radiators and hot and cold water feeds are all bonded in the bathroom upstairs. All pipework is copper throughout the plumbing never been altered in 40 years except for a new boiler oh and removal of the water tanks. So can I be confident the bonding upstairs is good enough? 

Parents
  • John Peckham: 
     

     

     

    Kelly

    If you have seen an electrode laying next to the joint in the ground that is almost certainly a PME supply. The DNOs should/maybe lay an earth electrode next to a joint in a 3 phase cable on a PME service. 

     

     

    John unfortunately in the SSEN area (at least the old Wessex division ( where Kelly is)), an earth rod was often added connected to the lead sheath.

Reply
  • John Peckham: 
     

     

     

    Kelly

    If you have seen an electrode laying next to the joint in the ground that is almost certainly a PME supply. The DNOs should/maybe lay an earth electrode next to a joint in a 3 phase cable on a PME service. 

     

     

    John unfortunately in the SSEN area (at least the old Wessex division ( where Kelly is)), an earth rod was often added connected to the lead sheath.