Very long run of LV Cabling

Hi all,

 

im looking at a project where the landlords LV cut out is approx 850 metres from the proposed tenants installation. The earthing arrangement is TT and protected by a time delayed 300ma RCD and a 63A MCCB.

 

The landlords sub main is going to be 2 x 4C 95mm2 in parallel buried in the ground to supply 20KVA worth of power. This achieved a volt drop of 1.6% which leaves 1.9% VD for lighting. From my Amtech calcs I also get about 1ka at the load Dis board (Phase fault)

 

im not worried about Earth Loop because of the RCD, but i am thinking about the adibatic of the phase conductors. If the tenant puts a long run of cabling in, this will comply from a Zs perspective, but could there be issues with the line under a phase to neutral /phase to phase fault as the cable could slowly cook under a lowish load without tripping the breaker. Is this a valid concern? Amtech isn’t throwing up any faults, but just wanted your thoughts.

 

thanks in advance

Parents
  • If a generator is needed for two years, outright purchase is probably cheaper. After the two years it might be worth keeping it for standby purposes.

    If a generator is to be regularly used for two years, it might be worth utilising the heat from the engine cooling system for central heating. Free heating, apart from the cost of the plumbing works.

    Dont forget a battery bank for lighting, refrigeration, and small important power loads. Either with an inverter or specify ELV DC for lighting and refrigeration. It is exceedingly inconvenient to manage without electric lighting on demand these days.

Reply
  • If a generator is needed for two years, outright purchase is probably cheaper. After the two years it might be worth keeping it for standby purposes.

    If a generator is to be regularly used for two years, it might be worth utilising the heat from the engine cooling system for central heating. Free heating, apart from the cost of the plumbing works.

    Dont forget a battery bank for lighting, refrigeration, and small important power loads. Either with an inverter or specify ELV DC for lighting and refrigeration. It is exceedingly inconvenient to manage without electric lighting on demand these days.

Children
No Data