Hot tub installation

Hi guys I have a question on installing an outside supply to a spa at home. I have a few questions regarding this one is the consumer unit has no spare ways have checked maximum demand and all seems okay for an additional 32 amp load. My plan was to get a garage style CU and take out out of the 6 amp lighting circuit breakers at the main board and replace with a 40amp breaker to feed the new CU containing the lighting circuit and swim spa circuits. I’m then planning on running a 6mm swa outside to a rotary isolator. 
 

first question is does the new CU require surge protection? (I know this will have to be signed off by someone who is registered as I’m not registered)

 

Does the lighting circuit require an installation certificate as well? I’m presuming it will as I’m installing it in a new board. 
 

and lastly (I know there is many debates about this) but what are your guys thoughts on TNCS supplies and earth electrodes? I’ve been told by the manufacturer they’ve never heard of any electrician ask about using an earth electrode? 
 

thank you for your replies in advance 

Parents
  • It’s not an easy one. So it’s saying you can either create a TT island or use the PME earth with an additional earth electrode connected to the earthing system that’s under 20 ohms. Either way I know contact with true earth is going to be a problem. So i take it the TT island would be best. I don’t think 20 ohms is going to be easy to obtain. Isn’t there a value of 1667ohms if it’s protected by a 30ma RCD so as long as Earth loop is bellow this value?
Reply
  • It’s not an easy one. So it’s saying you can either create a TT island or use the PME earth with an additional earth electrode connected to the earthing system that’s under 20 ohms. Either way I know contact with true earth is going to be a problem. So i take it the TT island would be best. I don’t think 20 ohms is going to be easy to obtain. Isn’t there a value of 1667ohms if it’s protected by a 30ma RCD so as long as Earth loop is bellow this value?