Hi guys I have a question on installing an outside supply to a spa at home. I have a few questions regarding this one is the consumer unit has no spare ways have checked maximum demand and all seems okay for an additional 32 amp load. My plan was to get a garage style CU and take out out of the 6 amp lighting circuit breakers at the main board and replace with a 40amp breaker to feed the new CU containing the lighting circuit and swim spa circuits. I’m then planning on running a 6mm swa outside to a rotary isolator. 
 

first question is does the new CU require surge protection? (I know this will have to be signed off by someone who is registered as I’m not registered)

 

Does the lighting circuit require an installation certificate as well? I’m presuming it will as I’m installing it in a new board. 
 

and lastly (I know there is many debates about this) but what are your guys thoughts on TNCS supplies and earth electrodes? I’ve been told by the manufacturer they’ve never heard of any electrician ask about using an earth electrode? 
 

thank you for your replies in advance 

Parents
  • Isn’t there a value of 1667ohms if it’s protected by a 30ma RCD

    That's for ADS (the figure actually comes from ensuring that exposed-conductive-parts can't exceed 50V above true earth when the earth fault current/earth leakage is just too low to ensure the RCD will trip). But that's then subject to making sure that the TT electrode has sufficient contact with the lower layers of earth to ensure it's reliable over the seasons - which is often deemed to be reflected in a figure of less than 200 Ohms (or some prefer 100 Ohms).

    But none of that makes a blind bit of difference if your means of earthing itself is at a raised voltage (either due to voltage drop along the PEN conductor in the case of ‘perceived electric shock’, or a close to full mains voltage in the case of a broken PEN) - since the RCD won't disconnect the c.p.c. even if it did trip.

    I agree with Mike that 20 Ohms is a bit of a nonsense. I guess it's been copied from the practice of street lighting where max 20 Ohm electrodes are used to protect (to some extent) from broken PEN conductors - but that only work due to the very limited load currents (<2.5A to keep things below 50V) - which is fine for a street lamp or two, but hardly realistic for an entire domestic installation, especially one including an electrically heated hot-tub.

    A buried grid - to force the ground in the vicinity to the same voltage as the local earthing system makes a lot more sense (in that case the resistance to the general mass of the earth is of much less significance), but it would have to go under the entire area. And there are still risks around the edges of the area protected in that way.

    Life might have been so much simpler if the DNOs had stuck with TN-S.

       - Andy.

  • Life might have been so much simpler if the DNOs had stuck with TN-S.

    Each of the earthing arrangements has its issues.

    If we have a TN-S installation with no extraneous-conductive-parts (or extraneous-conductive-parts that don't have an extremely low fortuitous earth electrode resistance), and the supply protective conductor becomes damaged, one can still be left with hazardous touch voltage/touch current at exposed-conductive-parts due to the summation of protective conductor currents from appliance noise filters.

    Yes, with respect to wet barefooted persons, diverted neutral currents in PME systems can cause "tingles" in normal operation, and I agree this isn't ideal ... but TN-S isn't without its problems (nor is TT).

  • If we have a TN-S installation with no extraneous-conductive-parts (or extraneous-conductive-parts that don't have an extremely low fortuitous earth electrode resistance), and the supply protective conductor becomes damaged, one can still be left with hazardous touch voltage/touch current at exposed-conductive-parts due to the summation of protective conductor currents from appliance noise filters.

    Agreed - but dealing with a few tens or even a few hundred milliamps of leakage current seems relatively practical with say an additional electrode - much more so than the (dropped) proposal to do similar for PME systems.

    Quite agree about TT systems too - the Earthing system could be by at anything up to 50V above true earth and still be compliant with BS 7671 requirements - yet it's often suggested as a means of avoiding perceived electric shocks of 10V or 20V from a PME system.

       - Andy.

Reply
  • If we have a TN-S installation with no extraneous-conductive-parts (or extraneous-conductive-parts that don't have an extremely low fortuitous earth electrode resistance), and the supply protective conductor becomes damaged, one can still be left with hazardous touch voltage/touch current at exposed-conductive-parts due to the summation of protective conductor currents from appliance noise filters.

    Agreed - but dealing with a few tens or even a few hundred milliamps of leakage current seems relatively practical with say an additional electrode - much more so than the (dropped) proposal to do similar for PME systems.

    Quite agree about TT systems too - the Earthing system could be by at anything up to 50V above true earth and still be compliant with BS 7671 requirements - yet it's often suggested as a means of avoiding perceived electric shocks of 10V or 20V from a PME system.

       - Andy.

Children
  • Earthing system could be by at anything up to 50V above true earth and still be compliant with BS 7671 requirements

    But in a system with a 30mA RCD, as required for safety of life, and almost any electrode system that is much more than the end of a wire in a flower pot, will do better than the 1500 ohms or so that would give a 50V offset, probably by a factor of ten or better.

    So regs wise I agree, the voltage could be 49.99V, but is quite likely to be less than 5V, even with a fault in progress at a level that is certain to trip the RCD in a fraction of a second. Assuming the RCD is not to false trip, then a leakage more like 10mA should be seen as an upper limit if all is operating exactly as it should, so perhaps 1 to 2V when  in normal operation ?

    On real TT systems, the offsets are often very low indeed - often non 50Hz components from elsewhere are dominant.

    Mike.

  • But in a system with a 30mA RCD, as required for safety of life, and almost any electrode system that is much more than the end of a wire in a flower pot, will do better than the 1500 ohms or so that would give a 50V offset, probably by a factor of ten or better.

    A single RCD yes, but what about multiple RCDs - e.g. a CU with a dozen or more 30mA RCBOs as tends to be the fashion these days?

    Hopefully normal protective conductor currents will be small, but all it needs it a bit of wet getting in somewhere (e.g. an outside light or socket) and such assumptions can count for naught.

       - Andy.