Good afternoon

Does anyone know if BS9999 poses a limit in the number of seconds between a power failure and the generator taking full load on?

Unfortunately I do not have access to BS9999 at this moment and I cannot remember the answer of the top of my head so please excuse my question

Thanks

Parents
  • Hi Apostolos. It's 15 seconds;

    f7b2a2c0456b794479fbe9a407a71bd1-original-image.png
    BS999: 2017

    Regards, burn