The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Maximum demand calculation

Hi, 

I am trying to calculate a realistic and sensible maximum demand for a project:

Ring final (kitchen) - 32A (100%) 

Socket radial 1 - 20A 

Socket radial 2 - 20A 

Socket radial 3 - 20A 

Lighting 1 - 10A (2A) 

Lighting 2 - 10A 2A) 

EV charger (with load curtailment) - 40A 

Cooker - 15.3Kw = 10A + (30%) 16.95 = 27A. 

Can anyone advise what should be applied to the socket radials? These cover sockets on the ground and first floor of the property. I have allowed 100% of the kitchen ring, but what would be appropriate for the other radial socket circuits?

I am temped to treat them all as a single 32A ring circuit, and base this on the 40% value, equalling 12.8A.

Am I also safe to allow 40% for the kitchen ring, this allowing a maximum socket outlet value of 25.6A? 

Thanks. 

 

 

Parents
  • It may help to consider how much floor area are you serving - there is a limit to the number of kW anyone will dissipate in a small space for very long without overheating and turning things off - the 32A per 100m2 rule may be more realistic for domestic regardless of how many circuits  it is divided over.

     

    is the 2A the real max load on the lights? - if it is LED or even CFL, you get a lot of lighting for an average current of an amp. 

    Mike

Reply
  • It may help to consider how much floor area are you serving - there is a limit to the number of kW anyone will dissipate in a small space for very long without overheating and turning things off - the 32A per 100m2 rule may be more realistic for domestic regardless of how many circuits  it is divided over.

     

    is the 2A the real max load on the lights? - if it is LED or even CFL, you get a lot of lighting for an average current of an amp. 

    Mike