for instance, using 5x20 1A Fast Ceramic Fuse 250V in an installation ...

Good evening folks - thoughts/advice please

 

… is there a British Standard for these types of fuses ?

… how would using them in circuit sit regarding BS7671 ?

 

Regards

Habs

Parents
  • In my view, the limited breaking capacity of these small fuses means that they should not be used directly from the incoming supply, nor from a large sub main with a similar load capacity and potential fault current to a DNO supply.

    They may, in my view be used  to protect small loads that are connected to a sub-circuit.

    To connect a clock, small extract fan, emergency light, or the like to a 6 amp circuit, or any size circuit up to say 32 amps.

    But not suitable for use in a consumer unit, or other equipment connected directly to the incoming DNO supply.

    Also suitable for use within equipment that is connected to the supply via a relatively small OCPD.

    If a one amp fuse is required for direct connection to the DNO, or other similarly large supply, then in my view a physically larger fuse with a larger breaking capacity should be selected. Such as a BS 88 type.

Reply
  • In my view, the limited breaking capacity of these small fuses means that they should not be used directly from the incoming supply, nor from a large sub main with a similar load capacity and potential fault current to a DNO supply.

    They may, in my view be used  to protect small loads that are connected to a sub-circuit.

    To connect a clock, small extract fan, emergency light, or the like to a 6 amp circuit, or any size circuit up to say 32 amps.

    But not suitable for use in a consumer unit, or other equipment connected directly to the incoming DNO supply.

    Also suitable for use within equipment that is connected to the supply via a relatively small OCPD.

    If a one amp fuse is required for direct connection to the DNO, or other similarly large supply, then in my view a physically larger fuse with a larger breaking capacity should be selected. Such as a BS 88 type.