Good evening folks - thoughts/advice please
… is there a British Standard for these types of fuses ?
… how would using them in circuit sit regarding BS7671 ?
Regards
Habs
Good evening folks - thoughts/advice please
… is there a British Standard for these types of fuses ?
… how would using them in circuit sit regarding BS7671 ?
Regards
Habs
In my view, the limited breaking capacity of these small fuses means that they should not be used directly from the incoming supply, nor from a large sub main with a similar load capacity and potential fault current to a DNO supply.
They may, in my view be used to protect small loads that are connected to a sub-circuit.
To connect a clock, small extract fan, emergency light, or the like to a 6 amp circuit, or any size circuit up to say 32 amps.
But not suitable for use in a consumer unit, or other equipment connected directly to the incoming DNO supply.
Also suitable for use within equipment that is connected to the supply via a relatively small OCPD.
If a one amp fuse is required for direct connection to the DNO, or other similarly large supply, then in my view a physically larger fuse with a larger breaking capacity should be selected. Such as a BS 88 type.
In my view, the limited breaking capacity of these small fuses means that they should not be used directly from the incoming supply, nor from a large sub main with a similar load capacity and potential fault current to a DNO supply.
They may, in my view be used to protect small loads that are connected to a sub-circuit.
To connect a clock, small extract fan, emergency light, or the like to a 6 amp circuit, or any size circuit up to say 32 amps.
But not suitable for use in a consumer unit, or other equipment connected directly to the incoming DNO supply.
Also suitable for use within equipment that is connected to the supply via a relatively small OCPD.
If a one amp fuse is required for direct connection to the DNO, or other similarly large supply, then in my view a physically larger fuse with a larger breaking capacity should be selected. Such as a BS 88 type.