Consumer unit tails hidden in void under stairs

Hi

I did a consumer unit change in Friday including upgrading the tails from 16mm to 25mm.

The tails ran from an outside meter box, through the wall and then for about 70cm through a void formed by lower third of under stairs space being boxed in by brick walls, then going in to the back of the consumer unit.

The tails were clipped around the edge inside the meter box and held in a clamp inside the consumer unit; therefore well supported at both ends. But I have reused the concealed run and they are unsupported inside the void.

The only other options I could see would have been run them as armoured cable inside the void or in the outside of the house. For both options I would have created significant disruption and significant work.

Just wondering what others would have done in this situation.

Thanks

Alan

Parents
  •  But I have reused the concealed run and they are unsupported inside the void

    Is your main concern about the unsupported run Alan? I personally would not worry about that. You could always affix warning labels if you think that somebody may disturb the hidden tails or damage them in the future. Evidently the previous tails survived the route well for some time.

    Could the mechanical protection required by 522.6.204 (iv) be the building structure itself, e.g. brickwork etc?

    Z.

Reply
  •  But I have reused the concealed run and they are unsupported inside the void

    Is your main concern about the unsupported run Alan? I personally would not worry about that. You could always affix warning labels if you think that somebody may disturb the hidden tails or damage them in the future. Evidently the previous tails survived the route well for some time.

    Could the mechanical protection required by 522.6.204 (iv) be the building structure itself, e.g. brickwork etc?

    Z.