We must maintain mechanical and electrical continuity of steel conduit, so can't use P.T.F.E tape or Loctite 55 at screwed joints to keep them watertight. Has anyone ever had water ingress at screwed conduit joints outside? 543.3.6.

Parents
  • Install the galvanised conduit as normal, ensure all joints are properly tight and spray all joints with galv spray. (much easier than painting it on by hand) 

    On the conduit boxes use a rubber gasket. 

Reply
  • Install the galvanised conduit as normal, ensure all joints are properly tight and spray all joints with galv spray. (much easier than painting it on by hand) 

    On the conduit boxes use a rubber gasket. 