We must maintain mechanical and electrical continuity of steel conduit, so can't use P.T.F.E tape or Loctite 55 at screwed joints to keep them watertight. Has anyone ever had water ingress at screwed conduit joints outside? 543.3.6.
3. - Conduit systems must be designed and erected so as to exclude moisture, dust and dirt. This means that they must be completely closed, with box lids fitted. To ensure that condensed moisture does not accumulate, small drainage holes must be provided at the lowest parts of the system.