The organs of Time delay fuses and C/D type MCBs what inside

 

Two similar problems occurred recently both were resolved but would like learned persons on the forum just to run an  eye over the MCB tripping problem scrutiny in other words,  if any  deviation from the none statutory BS7671has taken place.

A garage with a paint shop compressor motor failed, very old 3phase motor tested and condemned by me. He got a new motor and connected it up but it was a 5HP instead of 3.5HP, the difference in size of the new motor (smaller) than the old motors is remarkable .However it ran for a while then two 32 amp fuses blown in a three- phase supply main -switch . I did a temporary fix of placing a 30amp melt able link (fuse wire) across the fuses that I still carry from the old days saying I will be back with three dual element fuses in a week or two , did replace the temporary fix 3 HRC 30 amp motor fuses  £12 + vat. Goes to show the old fuse wire like the dual element HRC has an over current limit and a time delay before activation.

The second problem, due to ill health a garage mechanic gave up his rented garage, but still wanted to do small jobs in his home garage, he transferred his single phase motor compressor to the home garage which had two 13amp double sockets, he sent for me because the garage MCB kept tripping 20 amp type B, I changed it to a 32amp type C, problem solved. My question is there any reference in BS7671 as to fitting a C type MCB in a domestic ring main. The only danger I can think on is to check for a robust mains supply RCD is there a sequence of past events leading to problems.  

jcm 

 

 

  • Q2: why not a 20 A C type? What size cable? I would expect a 13 A BS1362 fuse to blow (every now and again) on start-up. “Ring” implies 2.5 sqmm cable. If Zs ≤ 0.68 ohms (measured ≤ 0.54 ohms) all should be well.

    Q1: 5 HP = 3.75 kW = 1.25 kW per phase = about 5 A. The start-up current could be (briefly) 6 times higher, but it ought not to be blowing its OCPD.

  • There is nothing as far as BS7671 is concerned that says B types are domestic and C types are commercial, though some folk talk as if there is. But to meet the same disconnection times a C type breaker needs something like half the loop impedance of its B-type brother. Of course for a modern 13A socket circuit, there should be an RCD in the offing, so even if Zs was a bit on the high side the RCD will make the ADS  fast  enough to be safe.

    Did you check the Zs and verify the RCD ?

    Mike