Hi, I have recently had a couple of EICRs performed for rental properties and on the report the inspector has put the following coding of C2 as there is no SPD fitted. 

“Inspection Schedule Item 4.20: Confirmation of indication that SPD is functional (651.4) is in a potentially dangerous condition. Urgent remedial action is required. ”  - C2

The consumer units are standard 18th edition purchased at screwfix within the last 3 months with both RCD & MCB protection but with no SPD's.  When I questioned this with the electrician that inspected, he told me that new legislation had recently come in that SPD's must now be fitted. Is this correct?

 

 

 

 

 

 

Parents
  • The sort of SPD that gets fitted to  consumer unit is not there to save lives.  If lightning strikes the building, the SPD will be gone long before you are.

    It is there to clip short duration over-voltages of the kind that sometimes damage cheaply made (but sometimes expensive ) electronics. such spikes and surges arise from inductive loads being switched and perhaps lightning strikes miles away.  Traditional components like motors wire-wound transformers and immersion heaters are not affected by them anyway.

    There is no way that its absence is a potential danger to life, unless perhaps you have some sort of life support equipment plugged in and then really a UPS is a better idea.

    I think maybe someone wants to bill you for some work, perhaps the inspection fee was a set competitively  low on the assumption of finding something?

    Surely there are other things wrong?

    Mike.

Reply
  • The sort of SPD that gets fitted to  consumer unit is not there to save lives.  If lightning strikes the building, the SPD will be gone long before you are.

    It is there to clip short duration over-voltages of the kind that sometimes damage cheaply made (but sometimes expensive ) electronics. such spikes and surges arise from inductive loads being switched and perhaps lightning strikes miles away.  Traditional components like motors wire-wound transformers and immersion heaters are not affected by them anyway.

    There is no way that its absence is a potential danger to life, unless perhaps you have some sort of life support equipment plugged in and then really a UPS is a better idea.

    I think maybe someone wants to bill you for some work, perhaps the inspection fee was a set competitively  low on the assumption of finding something?

    Surely there are other things wrong?

    Mike.