EICR - No SPD Coded C2

Former Community Member
Former Community Member

Hi, I have recently had a couple of EICRs performed for rental properties and on the report the inspector has put the following coding of C2 as there is no SPD fitted. 

“Inspection Schedule Item 4.20: Confirmation of indication that SPD is functional (651.4) is in a potentially dangerous condition. Urgent remedial action is required. ”  - C2

The consumer units are standard 18th edition purchased at screwfix within the last 3 months with both RCD & MCB protection but with no SPD's.  When I questioned this with the electrician that inspected, he told me that new legislation had recently come in that SPD's must now be fitted. Is this correct?

 

 

 

 

 

 

Parents
  • Former Community Member
    0 Former Community Member

    If the properties have brand new CUs, an EIC could only have been issued if they were compliant

    1. Why didn't the enforcing body who required the EICRs not accept the EICs?
    2. If the EIC's were not issued, why didn't the inspector observe this on his EICR?
    3. If the EICs were not issued, why not?

    Regards

    BOD

Reply
  • Former Community Member
    0 Former Community Member

    If the properties have brand new CUs, an EIC could only have been issued if they were compliant

    1. Why didn't the enforcing body who required the EICRs not accept the EICs?
    2. If the EIC's were not issued, why didn't the inspector observe this on his EICR?
    3. If the EICs were not issued, why not?

    Regards

    BOD