EICR - No SPD Coded C2

Former Community Member
Former Community Member

Hi, I have recently had a couple of EICRs performed for rental properties and on the report the inspector has put the following coding of C2 as there is no SPD fitted. 

“Inspection Schedule Item 4.20: Confirmation of indication that SPD is functional (651.4) is in a potentially dangerous condition. Urgent remedial action is required. ”  - C2

The consumer units are standard 18th edition purchased at screwfix within the last 3 months with both RCD & MCB protection but with no SPD's.  When I questioned this with the electrician that inspected, he told me that new legislation had recently come in that SPD's must now be fitted. Is this correct?

 

 

 

 

 

 

Parents
  • In a recent check, less than 12.5% of certain installations were found to be compliant with BS7671. Presently the number of “proper competent” EICRs is probably similar. Obviously, we need to re-assess “competent” with a rather better definition.

Reply
  • In a recent check, less than 12.5% of certain installations were found to be compliant with BS7671. Presently the number of “proper competent” EICRs is probably similar. Obviously, we need to re-assess “competent” with a rather better definition.