EN 61000-3-11 and EN 61000-3-12

Let's start by guessing what the appliance is that these instructions apply to.

Parents
  • There was another electrician at the same house at the same time,  I was in a bathroom and he was in the kitchen. 

    He read that and said "if that's a required loop measurement it's not going to happen".

    This seems to be above my paygrade. 

  • The issue appears to only affect larger units > 9 kW. The installation instructions say:

    1 The water heater must only be connected to a
    230-240V ac supply. If you are installing a
    water heater with a kilowatt rating above 9kW,
    it is advisable to contact the local electricity
    supply company.

Reply
  • The issue appears to only affect larger units > 9 kW. The installation instructions say:

    1 The water heater must only be connected to a
    230-240V ac supply. If you are installing a
    water heater with a kilowatt rating above 9kW,
    it is advisable to contact the local electricity
    supply company.