After an old PILC cable went pop under a pavement outside, myself and a few neighbours are now temporarily supplied by a DNO generator, which has got me wondering...

The generator seems to have no obvious Earth electrode ... how are they Earthing the system? In my case it's spliced into the remaining few 10s of metres of PILC cable so the lead sheath/armour is probably providing fairly decent connection with true Earth, but what would they do in general - e.g. if more modern plastic sheathed cables involved?

The other though is that Zs/PFC from the generator is unlikely to be anything like that from the grid (and what the TN installations would have been designed for) - will the DNO have taken any precautions to ensure that ADS will still operate adequately? Perhaps and RCD on the generator? Or might resilience take priority?

   - Andy.

Parents
  • If the network contains any PME then an RCD is not possible, as it sees it as  an NE fault.

    A genset on skids in the mud may well be its own electrode of 50-100 ohms, and that will be augmented by bonding at the houses that have metallic services.

    The path through the terra-firma ground is not the main fault loop for blowing fuses - that is done via the neutral/ CPC .

    The sort of gensets that DNOs have on 'call-off' with the likes of Agrekko have earth fault relays, because all hire gen-sets do, but when used for network support they are likely to be either off or set to a level rather more than the likely neutral current,  to avoid the PME issue.

    A modest genset for a few houses may not blow a 400A fuse like the substation would, though a house fuse at  60A or 80A should be in reach if a bit slow,  but even  if the fuse does not blow the volts will collapse or the genset will stall, so it is an awkward and flickery problem  rather than a dangerous outcome.

    Mike.

  • DAMN!! I clicked a wrong sign to report this!!! SORRY!!!! 

  • That letterbox  is indeed a class act. Had they said something to upset the team I wonder ? (shades of the ununlucky Mr Meldrew). Traditional way in would  be a fanlight window and if needed a couple of bits of chipboard one inside one outside screwed together to form a clamp to stop the draught.  I imagine there is no reg broken, apart from the one about good practice, but the earth rods look a bit shallow and rather close to each other to get the low ze  benefit of parallel connections.

    Mike

  • Thanks Mike... I just laughed, when I noticed this. 

    regards...

  • Cables through letterboxes are in my experience a common approach in this situation. Almost every home has one so it is a simple and quick way of restoring power.

    Drilling holes takes longer and risks damage.

  • https://www.youtube.com/watch?v=lNEXWITxkmg

    May be of interest, cables through letterboxes for some customers. Others restored by temporary connection of generators into the street mains.

  • Fair enough... thing was I haven't seen that done before. At least they had power!

    regards...

  • Have done it that way in the past when I worked for a DNO even used 6.0mm t&e.

  • Something to be to be aware of from the customers point of view, is that two approaches exist for temporary supply from a generator.

    Firstly is an extension lead, probably with a 32 amp male plug and several 13 amp sockets, the other way is a temporary cable connected in place of the usual service cable.

    The extension lead is less convenient since only appliances plugged into this lead can be used.but has the merit that the supply is not metered, a significant saving in some cases.

    The temporary cable in place of the usual service cable will energise the whole installation as normal, but the power passes through the KWH meter and is charged for.

    I once had a 32 amp extension lead for a week, free electricity for a week. though limited to 32 amps. I plugged into this lead my existing UPS, a couple of 1.5 kw heaters  and either the washing machine, or any other heavy loading appliance, or another heater.

  • Thanks guys.

    This generator seemed to be on wheels - two pneumatic and one solid rubber jockey wheel - so no fortuitous earthing there I fear - especially as it was on the hard road surface (if  a rough unadopted one) rather than mud. I'm pretty sure both water and gas in the neighbourhood are plastic (I happened to have retained a few metres of the old lead water pipe and kept it bonded as an attempt at an additional electrode, but the DNO probably wouldn't have known that).

    Good point about PME - the genny did have 5 separate cables from it, and my supply is certainly 'presented' as TN-S - so it might be they were able to treat it as proper TN-S ... but there might have been a N-PE link somewhere (supply to the street light perhaps). I guess we won't know now. My garage is TT'd and I was very tempted to do a loop test just to see how it differed from the normal supply ... but was put off my the fear of tripping out the supply for the rest of the neighbours.

      - Andy.

  • The usual is an earth electrode, although the System Neutral usually makes a better alternative. The temporary supply cable is usually terminated on a cutout mounted on a meter board. We would normally cut a slot in a meter box door, then mount the temp cutout next to the usual one - this is why we don't want customer equipment in the meter box!

    With a cutout inside, "through the letterbox" is the best and easiest option, and would be first choice. With a "temporary" between two houses, it is not unknown to have a temporary cutout on both ends of the cable, go out one letterbox and back in through next doors. 

    Regards,

    Alan. 

Reply
  • The usual is an earth electrode, although the System Neutral usually makes a better alternative. The temporary supply cable is usually terminated on a cutout mounted on a meter board. We would normally cut a slot in a meter box door, then mount the temp cutout next to the usual one - this is why we don't want customer equipment in the meter box!

    With a cutout inside, "through the letterbox" is the best and easiest option, and would be first choice. With a "temporary" between two houses, it is not unknown to have a temporary cutout on both ends of the cable, go out one letterbox and back in through next doors. 

    Regards,

    Alan. 