Hi All.

I have a situation where a resident has requested the installation of an EV Charger to their domestic premises which has a driveway.

The company installing (Large well known French energy provider) has refused to install the EV Charger as they have identified that there is a street lighting column located within 2.5m of the driveway with a PME service installed.

Whenever we have EV CHargers installed on the Highway we use a TT service and any associated street furniture located within 2.5m of the parking bay is also converted to a TT system. However - as this is a private household and the street light is already in situ it has caused an issue.

I have read the BS7671, 4th Edition of the Electric Vehicle Charging Equipment Installation and other relevant documentation but this apparently seems to be omitted from all publications. (Or have I missed something?)....  This is the first instance we have received of this nature but no doubt it will not be the last.

Any advice / comments welcommed.

Regards

Parents Reply Children
  • But if the charging point is TT, then the charging point and vehicle will be on a different earthing system to the street lamp.

  • I understood that Larryinplymouth had said that both the house and street lamp were PME.