High earth loop impeance at Transformer

Hi There, 

We have just installed a new 800kVA transformer on site with a impedance of 4.75%. However when it comes to taking the EL reading at source we are getting 0.12-0.14ohms compared to what we expect of 0.01-0.02 ohms. 

Other than checking the cable connections, changing the meter or having faulting TX can anyone give me some ideas why this may be. Has anyone come across this before?

Parents
  • This is a private Transformer which sits on a PWN. As part of the commissioning process as the TX has just been installed they have tested it and the results are high. But i agree i believe this to be a meter issue. 

Reply
  • This is a private Transformer which sits on a PWN. As part of the commissioning process as the TX has just been installed they have tested it and the results are high. But i agree i believe this to be a meter issue. 