Local isolator near drive, good or bad?

We have been asked by operations to look at streamlining isolation tasks for mechanical and process jobs. 

I have suggested having local isolators next to the required drives (belt driven fans / pumps etc), which can be operated by anyone, instead of MCC located isolators or even fuse pulling, done by specifically trained people.  

I cannot find anything about best practice or pro/cons on something like this, so I a hoping people here could offer advice?

Parents
  • This is something we now do as standard at the site I work at for exactly the reasons specified. We also have two levels of isolation though, one that any trained technician can do that is appropriate for mechanical non-intrusive work and one that only competent Electricians can complete for Electrical work or intrusive maintenance. This stops people from relying solely on the isolator when working on circuits or with their hands in machinery etc.

    We also use auxiliary connections in the local isolators as an interlock with the control circuit to prevent the isolators from being used to start and stop the drive. Some isolators come with early break contacts specifically designed to stop a motor control circuit before the main contacts are opened to prevent the device being used on-load.

  • I would expect a formalised procedure is in place also with a written Permit to Work system.

    Jaymack 

Reply
  • I would expect a formalised procedure is in place also with a written Permit to Work system.

    Jaymack 