I don't think there's a blanket "not advised".
PME Earthing does pose some challenges, which should be taken into consideration. Usual reasons for not using a PME earth might include:
otherwise you're normally quite free to use extend the main building's earthing out to an outbuilding.
- Andy.
If you had it you'd also use the outbuilding rebar, or steel piles or any other metal that was in the ground or in concrete in the ground that was part of the building. A lone spike as such is the least you can have.
Now you can and would extend the house earth to any old outbuilding if the supply was TT or TNS, the only problem is that a great many areas are wired with a supply earthing that is TNC-s (PME) and I presume you live in one of them.
So with PME the system earth is really the DNO neutral - and is very good as a CPC for blowing fuses if there is a live to earth fault, but it is not guaranteed to be at the same potential as the ground outside - the "terra-firma" earth voltage if you will. For garden tools, being pretty much always double insulated we do not care, but a supply to an earthed object that can be touched is a bit of a stickier wicket. The risk varies and so does the advice about how best to organise the earthing. Not all cases are equal.
The newest panic is some one in bare feet on wet grass touching a metal car door handle while it is plugged into an EV charger. Things like painted lamp posts are less of a hazard, and tend to be in part their own electrode. For years folk have wondered about mains supplies into caravans and boats.
As above a building with an earth floor, like a barn, or a damp concrete floor, like some garages, poses a similar hazard, but things that are free draining and hostile to bare feet (gravel perhaps) are less of an issue.
So what is in this outbuiding, how is it constructed and how is it to be used, and it may or may not be OK on a PME system, or best moved to TT.
Mike.
If you had it you'd also use the outbuilding rebar, or steel piles or any other metal that was in the ground or in concrete in the ground that was part of the building. A lone spike as such is the least you can have.
Now you can and would extend the house earth to any old outbuilding if the supply was TT or TNS, the only problem is that a great many areas are wired with a supply earthing that is TNC-s (PME) and I presume you live in one of them.
So with PME the system earth is really the DNO neutral - and is very good as a CPC for blowing fuses if there is a live to earth fault, but it is not guaranteed to be at the same potential as the ground outside - the "terra-firma" earth voltage if you will. For garden tools, being pretty much always double insulated we do not care, but a supply to an earthed object that can be touched is a bit of a stickier wicket. The risk varies and so does the advice about how best to organise the earthing. Not all cases are equal.
The newest panic is some one in bare feet on wet grass touching a metal car door handle while it is plugged into an EV charger. Things like painted lamp posts are less of a hazard, and tend to be in part their own electrode. For years folk have wondered about mains supplies into caravans and boats.
As above a building with an earth floor, like a barn, or a damp concrete floor, like some garages, poses a similar hazard, but things that are free draining and hostile to bare feet (gravel perhaps) are less of an issue.
So what is in this outbuiding, how is it constructed and how is it to be used, and it may or may not be OK on a PME system, or best moved to TT.
Mike.