The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Electric shock through live apparently earthed metal face plate.

A friend asked me to check electrics at a house his daughter had just moved in to last Friday.  They had been getting shocks from a metal light switch so had been using their sleeve to turn it on and off can you believe.  He went round for another reason and touched it and got a nasty belt, his hand was still aching when i arrived twenty minutes after.  I popped one prong of my two prong tester on it and it buzzed to indicate it was live, i didn't confirm it was a full 230v as there wasn't an easy place for the other prong.                                                                                I turned the power off and removed the switch, it appears that one of the cores had scagged the south lug which hadn't been bent out the way.

 What confuses is me as to why the circuit breaker did not trip as it appears that it was a dead short although there was no blacking of the cable where it looks like it touched the lug, just a deep dent in the insulation.

 I confirmed the earth continuity as i initially thought that the earth had to be missing.There was also a fly lead.  The building is an old farm house although this part was in a newer extension with a sub-main and dedicated  CU.  there are no rcd's in the building.  The installation was apparently sold by an electrician, there was a nice inspection and test label at the CU dated Sept 2021 but no actual report that they know of.  

I have recommended they have the consumer units updated.   

It had a PME earth

Gary                                                                                               

Parents
  • how did you verify the earthing of the back box, and to what ? Connection verified to MET may or may not mean connection to the supply neutral.

  • After i had removed the face plate i noticed a socket on the wall pretty close and did a simple continuity check over to the lug.  I did a loop test at the socket to confirm a decent earth connection , this was around 0.6Ω. 

    I will be doing an EICR in the new year and they have asked me to quote to upgrade the CU's as well.

Reply
  • After i had removed the face plate i noticed a socket on the wall pretty close and did a simple continuity check over to the lug.  I did a loop test at the socket to confirm a decent earth connection , this was around 0.6Ω. 

    I will be doing an EICR in the new year and they have asked me to quote to upgrade the CU's as well.

Children
No Data