Do I need to do anything about single pole Isolator owned by DNO

I was changing a consumer unit today on a property where there was an isolator supplied by the DNO (owned by _______ molded in to it) but it was only single pole. The supply was TNCS and the consumer unit has a double pole isolator. The property is about to be put on to the rental market.

My initial thought is that the double pole isolator switch in the CU provides the isolation function and its a TNCS supply with limited risk of dangerous voltages on the Neutral. Therefore the single pole isolator upstream of the CU isn't ideal but not immediately dangerous and I should just note it on the installation certificate.

Or should I be highlighting the problem to the owner and suggesting they contact their DNO to request a change and what is the likely response from the DNO?

Looking forward to your views and advice.

Thanks

Parents
  • I just had another quick look on YouTube for the IET video, but cannot see it.

    It prompted me to buy a single pole contact voltage indicator, I used it a few weeks ago when I did a call out for a gas contractor replacing the old metal gas mains pipework with plastic, they disconnected the old steel gas pipe and the meter became live as did everything else that should have been earthed in the house, because the old gas main was the earth electrode for the TT installation.

    Do not trust either a single or double pole switch to truly isolate an electrical installation.

Reply
  • I just had another quick look on YouTube for the IET video, but cannot see it.

    It prompted me to buy a single pole contact voltage indicator, I used it a few weeks ago when I did a call out for a gas contractor replacing the old metal gas mains pipework with plastic, they disconnected the old steel gas pipe and the meter became live as did everything else that should have been earthed in the house, because the old gas main was the earth electrode for the TT installation.

    Do not trust either a single or double pole switch to truly isolate an electrical installation.