Can anyone offer experience on the application of Table 54.7 for Main Earth size on non PME supplies for supplies that have parallel incoming cables.
For example, 2 x 185mm2 PCV/SWA installed in separate ducts.
Thanks
I believe the answer to this question is:
The use of Table 54.7 for parallel cables is not applicable and the adiabatic must be used when faced with parallel cables.
With 2 cables I think you can get away with it as you can install a cable equal to the main phase and it will be fine. When 3+ parallel cables are used it really is not the way to go.
I believe the answer to this question is:
The use of Table 54.7 for parallel cables is not applicable and the adiabatic must be used when faced with parallel cables.
With 2 cables I think you can get away with it as you can install a cable equal to the main phase and it will be fine. When 3+ parallel cables are used it really is not the way to go.