Has anyone had incidences of rod 'stats tripping off by the back-up safety cut off with no apparent reason. The copper cylinders had no secondary heating that could overheat the water such as a coil heated by gas or oil.
Z.
Yes! I had alot of trouble with this happening after I replaced our immersion heater last winter.
In trying to solve this turned down the thermostat to the min setting - it still randomly tripped.
I replaced the thermostat with a (identical) new unit - it still randomly tripped.
I replaced the entire immersion heater again - it still randomly tripped with both thermostats.
During this debugging process I modified the outlet on the hot water cylinder to allow me to insert a 300mm K-type thermocouple into the water. By logging this thermocouple I was able to prove that the water temperature never reached anyway even close to the 90C cout-out point of the over temperature trip - yet it still tripped!
Just when I was reaching the point of despair - it stopped tripping & has behaved itself since the spring (no, this doesn't coincide with the central heating being turned off!). The logging is still in place & have have noticed that the thermostat switch off point is slowly creeping upwards. We are in hard water area & i'm wondering if this is happening as things are slowly being covered in limescale.
where in the water is the thermostat measuring, and orientation of this relative to heater element ? just wondering if it matters if the heater and stat are one above the other in terms of convection - it may not be stirring itself as well as you think.
I did think about that... I tried rotating the the immersion such that the element was above the 'stat (this is a immersion mount on the side of the dome of the cylinder so it projects through the water at an angle) as well as above it - it didnt make any difference.
I did think about that... I tried rotating the the immersion such that the element was above the 'stat (this is a immersion mount on the side of the dome of the cylinder so it projects through the water at an angle) as well as above it - it didnt make any difference.
So, this evening, the water boiled!
I just happened to be in the right place at the right time - I heard the boiling start & the first of the steam bubbles come up the vent pipe! I quickly switched the immersion off so no real damage done.
The tank is way to hot to touch at the moment, the logging thermocouple is still showing 97C, but tomorrow I will have a closer look at the immersion heater thermostat. It will be interesting to see if the secondary over temperature cut-out has operated - I suspect not.