Hi all, got an interesting project, that I'm in the planning stages for.
There is a 3 phase supply in a small outbuilding that is to be exported to 2 houses (same owner on 1 site), the supply is 100A PME (0.35 ohms).
The PME will be exported via SWA armouring and a separate 35mm 6491x cable (to both houses for bonding and CPC)
The supply head, the first house and the second house are in a straight line so in effect an SWA cable can come from a switch fuse (100A) in the outbuilding, go to the first house and then loop out into the second. Due to the location of the buildings it wouldn't be practicle or economical for the DNO to bring the service head closer or more centralised.
The first house needs a 45m run of SWA and then there is a further 40m to the next house. I intend on using a 95mm 4 core SWA cable for the first 45m then terminate it in an enclosure and split off in 25mm 4 core into the first house and 50mm 4 core for the next 40m to the second house. The 50mm cable would be in a duct that is already buried and is the largest cable size that could be used and still realistically be pulled through.
Now the above works for the voltage drop requirements but I am having trouble with disconnection times as the first house would meet the required 5 seconds (just) but the second would not, as I can't increase the 50mm cable in size I'm thinking a time delay RCD protecting the whole instalation is the way to go? I hope that all vaguely makes sense ish! Thoughts would be appreciated, thanks!