Fluctuations in reading ZLine Ipscc

Hi,

 

It's been a long time since I have posted a question. However, have a ' live'  situation where I could use the advice of members, experts and sages on the IET forum.

 

Stated to work in a domestic property single phase supply TT system and when I tested the PFC on the short circuit, the test instrument gives fluctuations in reading from 0.01 ohms to 0.07 ohms

 

The meter has recently been callibrated and despite this: the thing is jumpy and  cannot give consistent readings. I accept that MFT have tolerances and this is a metrel with a resolution of 0.01 with an accuracy rating of -+5digits. So at low ohms it can fluctuate but still be in callibration

 

I have measured the PFC on the short circuit with a loop tester Martindale which is not  callibrated and this is giving a reading of 0.07 ohms.

 

A consumer unit has been installed which has 6ka breakers and I have checked with the manufacturers Contactum  and the board has a conditional rating of 16ka.  The supply fuse is Bs1361 type 2.

 

I have made enquiries with the DNO and they have confirmed that the substation is 50 meters away from the property, it is a 500kva transformers and the supply cable is a 0.1 concentric cable cable of 70mm

 

This is going to be my assessment job for the NICEIC

 

The question is this: from the DNO information how do I calculate the pfsc short circuit current

 

The second question, and this is gleaned from other forums, to achieve greater accuracy  in the  MFT, it has been suggested to introduce a known resistance. I have made test probes where I have placed a 10watt wirewound resistance of 0.68ohms and used this on the neutral conductor to undertake the test. It has given more consistent readings on the jumpy Mft  of 0.06 to 0.08 ohms when I have  deducted of the resistor value placed in the test lead

 

From a gs38 and guidance note 3 basis, would the above practice of placing a known resistor in the test leads be acceptable

 

I do not intend to undertake the measurement of the PFC with the make shift test probes with the resistor before the inspector, but do feel that in the field it would be method of attaining greater accuracy in testing

 

Apologies for the length of post but would like some advice.

Parents
  • Sorry I am a bit confused. How are you getting a PFC reading in ohms and not amps ?

    Gary

  • The figures stated is the impedance 0.02 to 0.07 ohms. To get the current it's u 230 / impedance....

  • I think Gary was just wondering why Ohms were given when most meters display Amps or kA directly on a PFC setting. (Granted it's generally the same test internally, but the meter does the calculation into amps for you (sometimes using 230V sometimes the actual voltage).

       - Andy.

Reply
  • I think Gary was just wondering why Ohms were given when most meters display Amps or kA directly on a PFC setting. (Granted it's generally the same test internally, but the meter does the calculation into amps for you (sometimes using 230V sometimes the actual voltage).

       - Andy.