BS88 Fuses

I am looking at the time/current characteristic of a 160A BS88 fuse which looks as though it will blow at about 260A after 70,000 seconds.

According to I^2*t, this lets through a hugh amount of energy, which would require a sizeable cable to withstand ?

I presume this is the maximum amount of energy this fuse will pass ?

I am new to this type of work, so probably reading this wrong.

Thanks Derek

Parents
  • 70,000 seconds is a very long time in the thermal world - the usual adiabatic equations are only good to around 5s - beyond that heat starts to be lost from the cable and you actually need a much smaller conductor than k²S² would suggest. If you applied the adiabatic to 160A and infinite time it would suggest you need an infinite c.s.a. cable - which clearly isn't correct or helpful.

    Generally relatively small overcurrents like this are regarded as overloads rather than fault currents - and in most cases simply ensuring that the cable's Iz is at least In is sufficient to ensure it's protected - there being suitable margins in the tables and construction of the cables to ensure reasonable safety (thermally at least). Small corrections might be needed for BS 3036 fuses and buried cables, where the margins are otherwise a bit thin.

       - Andy.

  • Hi Andy, thanks for getting back.

    It was the small overcurrent scenario I was thinking off.

    I didnt realise it only applied to short duration faults and not the small overcurrent scenario, which take can take hours to blow the fuse.

    Some good analogies above, for although the energy transferred for a small overcurrent may be large, it it the time overwhich it occurs keeps temperature rise down.

    Thanks, Derek

Reply
  • Hi Andy, thanks for getting back.

    It was the small overcurrent scenario I was thinking off.

    I didnt realise it only applied to short duration faults and not the small overcurrent scenario, which take can take hours to blow the fuse.

    Some good analogies above, for although the energy transferred for a small overcurrent may be large, it it the time overwhich it occurs keeps temperature rise down.

    Thanks, Derek