intermittent RCD tripping advice please

Hello there everyone,

I wonder if anyone would be kind enough to advise on the best course of action with a fault that my father has.

He’s had an intermittent RCD tripping fault since late last summer.

The RCD regularly trips anything from 2 hours to 4-5 days. There doesn’t appear to be any obvious reason for the trips - appliances, weather, time of day etc.

Installation is twelve years old and was all newly installed when their house was renovated. The CU is a Europa and has two rows of 10 slots, each with RCCB protection. The bottom row is the one that keeps tripping - top is fine.

They have had a few things added fairly recently like AC and a new microwave. The microwave seems the closest to the timeline of problems starting.

They do have a Whirlpool bath that needed a new control lead (low voltage logic control stuff), due to water rusting the male/female connector, but that has now been replaced - no water ingress to the main PCB control box. However, Dad found that when turning the bath supply back on that it would sometimes trip straight away, but normally it stays on when idle. I became suspicious of the bath when I learned of the rusted control cable and tripping and advised him to fully isolate the bath to see if the tripping stopped. Isolating the bath does seemed to have reduced the frequency of the tripping, but not stopped it (maybe it’s just adding a tad more leakage, which just pushes the RCD over the limit?). There are a few boxes under the bath (PCB control box, LED control box, air blower/heater). Note: the bath wasn’t connected when the latest IR test was performed. However, I’ve seen the power trip just by turning on their outside lights, for example.

First electrician came a few weeks ago and did some very basic testing. He was on his way home from another job and didn’t have much time. He tested the RCD, said it was fine, but replaced it anyway (Clipsal) to rule it out. He told Dad at the time that it was a N-E leak and that it could be anything causing it. He tried for a while to get him back, but he was too busy with an industrial install.

A different electrician visited this week and spent two hours there looking at the install. I had the chance to speak with him this morning. He said that the IR test didn’t look good on three of the circuits, which are all the ring mains. He didn’t test leakage. He tested the outdoor sockets which were all fine. Dad thinks the meter said 360 for one of the ring mains, but no idea if this is correct - take that with a pinch of salt! He also discovered that top RCD was stuck, but freed it and said it was fine (it hasn't tripped since, but the bottom has twice).

He recommended that Dad worked one room at a time, unplugging everything, leaving it for a week and using this approach to try and locate the problem. Dad isn’t keen on this as he’s a bit older and not the most technical person! However, I’m happy to spend some time there to do some testing, if it will help.

Given the randomness of the tripping, I asked him if he thought it might be caused by cumulative leakage across all the ring mains or a single faulty appliance. He felt it was a possibility.

When Dad wasn’t keen on the testing option, he suggested upgrading the existing CU with RCBOs. Cost is ~£700. As I believed would be the case, he confirmed that doing this won’t necessarily fix the problem, but it would potentially pinpoint the circuit - although, at this point, surely we are suspecting the ring mains, or in particular the two ring mains on the bottom CU row that trips. He told me that it is not cost effective for him to diagnose the fault, but he felt there was value in somebody like me doing the testing and was supportive of that idea.

Would it be worthwhile getting a clamp meter and testing all of the appliances on the ring mains - starting with everything connected to the sockets on the two ring mains of the bottom CU row that is tripping? I understand that I’ll need to adapt an extension lead so I can clamp just the L-N.

What about clamping the L-N at the CU, taking the background readings of the leakage? Could you leave the clamp on and then go around and unplug things one at a time, looking for a large drop and potential source of the problem(s)?

I can understand that you might have a faulty appliance on one ring main, but all three? Likewise, how likely would it be that all three ring main/circuit cables are damaged in some way?

Appreciate any insights, thoughts or advice on this problem.

Many thanks in advance,
Richard

Parents
  • Hi Richard,

    Would you able to post some clear pictures of all three ring mains ?

    There are couple of possibilities of RCD/RRCB tripping

    1) Faulty equipment

    Solution: Remove all the equipment from the wall sockets or any other electrical/electronic devices and then check if its keep tripping or stop tripping

    2) The socket its self is an electrical accessory, some time the twin /single socket creates a fault itself due to ageing or usage

    Solution : Its tiresome lengthy exercise but its worthwhile to check each socket by removing it completely

    3) R1+R2 reading + Insulation resistance test for troubleshooting the exact location of the fault

    Solution : I suggest to do R1 + R2 test on ring mains , if the reading is satisfactory then carry on insulation test, if the insulation test is fail then divide the circuit and do the insulation test from consumer unit to first socket/accessory point and from the first point to second socket/accessory point and carry on until it reach the last socket / accessory point to consumer unit. This will definitely reveal the fault with in the piece of a circuit.

    If the initial R1+R2 test fail then you can also find the exact location of the fault by adopting the same method I have explain above.

    Any question please reply me I will try my best to see how I will help you.

    Kindest regards,

    Syed Rizwi MSc CMgr ICT Tech MIET MCMI

Reply
  • Hi Richard,

    Would you able to post some clear pictures of all three ring mains ?

    There are couple of possibilities of RCD/RRCB tripping

    1) Faulty equipment

    Solution: Remove all the equipment from the wall sockets or any other electrical/electronic devices and then check if its keep tripping or stop tripping

    2) The socket its self is an electrical accessory, some time the twin /single socket creates a fault itself due to ageing or usage

    Solution : Its tiresome lengthy exercise but its worthwhile to check each socket by removing it completely

    3) R1+R2 reading + Insulation resistance test for troubleshooting the exact location of the fault

    Solution : I suggest to do R1 + R2 test on ring mains , if the reading is satisfactory then carry on insulation test, if the insulation test is fail then divide the circuit and do the insulation test from consumer unit to first socket/accessory point and from the first point to second socket/accessory point and carry on until it reach the last socket / accessory point to consumer unit. This will definitely reveal the fault with in the piece of a circuit.

    If the initial R1+R2 test fail then you can also find the exact location of the fault by adopting the same method I have explain above.

    Any question please reply me I will try my best to see how I will help you.

    Kindest regards,

    Syed Rizwi MSc CMgr ICT Tech MIET MCMI