Borrowing a cpc from another cct for lighting cct coded C2 in PE magazine codebreakers.

Just read in the above February mag the sparks has  borrowed the cpc

from another cable in the process of changing a kitchen into a utility room.,because the

lighting cct had no cpc.

Thought this was allowed under 543.1.2  if the borrowed cpc was of adequate size?

The article states"the 2 circuits are no longer seperate or individually isolatable,as they are

now linked".

                                                                                        Regards,

                                                                                              Hz

Parents
  • I haven't see the article, but I agree it sounds a bit odd. I can see the logic that the two circuits are not entirely separate (especially if you had a situation where large protective conductor currents were present) but I don't that not being "individually isolatable" as being a contravention of the regulations (unless there was a particular requirement for them to be so). After all we allow single pole MCBs on TT systems that require the N to be broken for isolation - so strictly speaking we'd have to revert to the main switch or shared RCCB to isolate a final circuit.

    c.p.c.s are often linked by shared extraneous-conductive-parts or supplementary bonding anyway.

    I'd admit I have been a little uncomfortable when I've had to "borrow" a c.p.c. from another circuit - mostly because of the danger of someone working on the other circuit disconnecting the c.p.c. without realizing the it could still be in use via the other circuit - but my solution to that was just a label at the CU.

       - Andy.

Reply
  • I haven't see the article, but I agree it sounds a bit odd. I can see the logic that the two circuits are not entirely separate (especially if you had a situation where large protective conductor currents were present) but I don't that not being "individually isolatable" as being a contravention of the regulations (unless there was a particular requirement for them to be so). After all we allow single pole MCBs on TT systems that require the N to be broken for isolation - so strictly speaking we'd have to revert to the main switch or shared RCCB to isolate a final circuit.

    c.p.c.s are often linked by shared extraneous-conductive-parts or supplementary bonding anyway.

    I'd admit I have been a little uncomfortable when I've had to "borrow" a c.p.c. from another circuit - mostly because of the danger of someone working on the other circuit disconnecting the c.p.c. without realizing the it could still be in use via the other circuit - but my solution to that was just a label at the CU.

       - Andy.