This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Neutral and Earth voltage with battery storage

Hi,

I have a battery storage system which is grid tied. This has been G98 registered. The battery has a grid tie and a UPS backup circuit.

The system works as expected, however when in UPS backup mode, I have noticed something that I need to clarify.

When in normal grid tied mode, the following voltages are recorded on the UPS output: 

L-N = 230V 

L-E = 230V 

N-E = 0V 

When in UPS mode, the following: 

L-N = 230V

L-E = 130V

N-E = 130V 

The manufacturer confirmed that when in UPS mode, a N-E link is made automatically and disconnected automatically. I have contacted them but being in China, they are slow to respond.

What I noticed, is that if you switch off loads on the UPS output, the voltage between L&E slowly increases to around 200V. I haven’t as yet tested to see if the same is apparent with N&E. 

Any ideas? This is an inverter so I am unsure if this sort of reading/phenomenon is normal? 

Thanks. 

Parents
  • Those voltages suggest to me that the N-PE link isn't being closed in island/UPS mode. Floating outputs aren't unknown in small ordinary UPS designs but as you've confirmed that the should be a N-PE link in place, it sounds like a fault to me.

       - Andy.

Reply
  • Those voltages suggest to me that the N-PE link isn't being closed in island/UPS mode. Floating outputs aren't unknown in small ordinary UPS designs but as you've confirmed that the should be a N-PE link in place, it sounds like a fault to me.

       - Andy.

Children
No Data